Engine General (Supplementary) USCG Question #1428 (Set 26)

In the illustrated single zone HVAC system, what prevents the simultaneous flow of steam through the preheat coil and flow of chilled water through the cooling coil? See Illustration GS-RA-09 Illustration GS-RA-09: the U.S. Coast Guard has not released this illustration.

Official USCG Answer & Rule Citation

Correct Answer: Option A — The supply air duct thermostat controlling the steam flow is set several degrees lower than the design off-coil temperature associated with the cooling coil.

To prevent energy waste and simultaneous heating and cooling, the preheat coil thermostat is set lower than the cooling coil's off-coil temperature. This ensures the preheater only activates when the air temperature falls below the required minimum, preventing the cooling coil from fighting the heat added by the preheat stage.