Marine Electrical Systems USCG Question #673 (Set 23)

As shown in figure "A" of the ungrounded distribution system with possible ground faults shown in the illustration, under what conditions would an outage likely occur due to a ground fault causing a circuit breaker to trip? EL-0129

USCG Exam Illustration EL-0129
USCG Examination Diagram: Illustration EL-0129
Official USCG Answer & Rule Citation

Correct Answer: Option A — two ground faults associated with different phases

Per 46 CFR Subchapter J and IEEE 45, an ungrounded marine electrical system tolerates a single ground fault without interrupting power. However, a second ground fault occurring on a different phase creates a direct line-to-line short circuit, causing protective circuit breakers to trip.

100% Free & Open Access — No daily limits, paywalls, or gated answers on BrightMariner.